P5 Status - Power and Load% Indicators

Power Indicator displays: 289 Watts, and Load% displays 32% quite constantly. My understanding is P5 is rated at 1000 watts. 289 watts should be 28.9% (real time).

Do I miss something? Or the indicators not 100% correct? Can you please explain? Thanks.

Welcome, Tam!

I suspect you are power a load with a relatively low power factor. This draws more current. I suspect this is what the load percentage reflects.

Elk said Welcome, Tam!

I suspect you are power a load with a relatively low power factor. This draws more current. I suspect this is what the load percentage reflects.


Thank you for your reply, Elk. My loads are the tube amps with big transformers so I guess they draws more current. The P5 displays current as 1.74A. Output voltage is 225V, so usage in kVA is 225*1.74 = 391.5 (kVA) (power factor = 291/391.5 = 0.74).

With the load% as 32%, I believe the max kVA by P5 is 391.5*100/32 ~1200 kvA. Is 1200kVA the rating of P5? Can you please confirm? Thanks.

sorry, I meant 1.2 kVA

1250 VA