Part 2 twenty 2Φ
So far the numbers had increased significantly just in using the 14/3 ‘extension cable’.
But now we’re running the numbers for the dedicated audio feed which uses standard romex solid 12/2 w/grnd, house wiring cable, out of a box, from the hardware store.
ExTech CT70 Audio Run

General CA10 Audio Run

Notice how ALL of the numbers have taken a giant mother may I step up and the reference stubby cable has been equaled or bested by the Shunyata cables in terms of the ASCC readings.
Also notice all the numbers with a yellow background.
This is the only set of tests using all of the cables, mostly because this ac source is what I have my amp and dac plugged into. So to test the other cables on this ac source I just used an unused plug-in at the box. And I really don’t want to move my carefully positioned in-use cables just to test them elsewhere. And as we’ll see it really isn’t necessary because the only other comparable ac source, I call the 1st Splice, isn’t really useable for the audio system due to location, and besides I’m saving that as a surprise for last…
But note that the Vd % listings have dropped from 5% (or more) down to 2-5% using the ‘extension cable’, and are now down to readings in the 1-4% range.
And the ASCC numbers have shot up again, with peak readings near the 1Ka range which is a 50% (or greater in some cases) increase, again.
And of course we now have a range of cables to compare to each other all being fed by my dedicated audio run ac source.
And judging by the amount of yellow background we can see that the majority of the peak readings all belong to 4 cables including the Marigo.
And true to form the 2 testers still have different readings between them.
We saw readings of ≈ 200 or 300 peak amps (depending on the testing device) being able to be delivered to my standard plug in the wall.
The current jumps up to ≈ 500 or 700 peak amps (depending on the testing device), from the ‘extension cable’.
And now we have the Audio Run with ≈1kA peak amps.
So on the post and pillar circuits we get ≈ 30K near instantaneous ‘watts’.
Then using a 14/3 ‘extension cable’ we get ≈ 72K near instantaneous ‘watts’.
And now the romex cable with 1kA x 120 volts we have ≈ 120K near instantaneous ‘watts’.
which is ≈ a 160% increase from the ‘extension cable’,
and a 400% increase from my post and pillar house wiring.
The reason that ‘watts’ is in semi-quotes is they really aren’t ‘real’ watts. Watts is a time domain measurement and in these tests we’re sorta only paying attention to a very small window of time.
This means the instantaneous power delivery has increased 400% by adding a dedicated romex run direct from the panel instead of using the post and pillar house wiring.
But lets look at the numbers for the particular power cables themselves.
This first part is a way of seeing the progression of improvement as the power cables I used became more ’sophisticated’.
And at the two extremes we have the reference Stubby and the AppCord, just like in all the previous tests.
The ASCC numbers from the CA10 run from 500 - 770 which is a ≈54% increase
while the CT70 runs from 0.75 - 1.03kA is a ≈37% increase
And so to consider the total current dumping capability,
Which is (500+770/2) = 635a x 120v ≈ 76K near instantaneous ‘watts’ (CA10)
And (750+1030/2) = 890a x 120v ≈ 106K near instantaneous ‘watts’ (CT70)
You can see why I can’t trust the specific numbers, but the trends continue to hold true and provide useful insights.
So now on to the rest of the cables.
As we move from cable #3 thru to #6 we see a gradual shift towards increasing ASCC numbers and decreasing Vd %’s
This represents a progression of improvement in how I made those DIY based cables using better materials and more advanced treatment options.
The % increases while small are significant in that the SQ change was noticed when the G-4r cable came in to focus. In fact it still is a reference cable for me.
So from .76 to .96Ka = 26% increase (CT70)
And from 550 to 680a = 24% increase (CA10)
Indeed the G-4r cable remains close to the best of the cables numbers in terms of ASCC, Vd%, &Ω measurements, albeit 1/2 step down.
Which leads to the top 3 useful cables, the 2 Shunyata cables and the Marigo cable.
This is where things get a bit murky in terms of trying to use the numbers from these devices to compare individual cables.
Likewise, both the Vd% and the impedance Ω readings between the 2 testing devices, are also somewhat murky.
Overall the trends are clear enough but the ‘accuracy’ of the numbers becomes the fly in the ointment, so to speak.
But having said all of this, we are talking ≈ 1Ka (or slightly less as measured by the CA10) from these ‘best of’ cables. This is roughly 50 times the ‘rated’ current that is protected by a 20amp breaker. Versus ≈ 10 times for the standard (post and pillar) house wiring.
This is a significant increase.
But wait there’s more…
JJ
Next up Part 2 twenty - two 2Φ